'''This documentation is for firmware version 2.x.x.'''
'''The documentation of version 1.1.1 you can find here [[Raindancer Firmware V1.x.x (English) | Raindancer Firmware V1.1.1]]'''
=Download=
=Download=
Zeile 17: Zeile 21:
The firmware has following '' 'Workflow' '':
The firmware has the following '' 'Workflow' '':
The Mower is in the charging station. The Mower drives from the charging station a predetermined distance along the perimeter to an area and then begins to mow after the chaos principle. The mowing time is approx. 130min-150min with the original Ardumowerkomponents. After the battery voltage has dropped to 23.7V, the robot looks for the perimeter cable and drives it to the charging station. Once in the charging station, the battery is charged. The next mowing operation is restarted via the mobile phone with a range command. (The robot can also be operated without a charging station.)
If the mower reaches the perimeter wire it will continue driving for approx. 20cm. Then the rmower drives back and will be further rotated at a random angle.
For the '' 'Perimetererkennung' '' a 128-bit signal is used. Therefore, the Raindancer transmitter (sender) software must be installed on the transmitter. 2 perimeter receivers are needed. As you approach the perimeter cable, the robot slows down.
For the '' 'Perimeterrecognition' '' a 128-bit signal is used. Therefore, the Raindancer transmitter (sender) software must be installed on the transmitter. 2 perimeter receivers are needed. As you approach the perimeter cable, the robot slows down.
If the robot does not recognize the signal for 2 seconds, it stops and switches off the motors. If it recognizes the signal again, it continues.
If the robot does not recognize the signal for 2 seconds, it stops and switches off the motors. If it recognizes the signal again, it continues. If the perimeter signal is too weak in the middle of the lawn, a GPS area can be configured. If the robot is in this area, it is assumed to be within the perimeter loop.
With the original motors and wheels, the robot drives at a speed of approx. 1200m / h.
Zeile 37: Zeile 42:
The firmware was optimized for '' 'not with the perimeter wire fenced obstacles' '' on the lawn. Instead of driving at full speed against the obstacle, the speed is reduced from a certain distance and drove gently against the obstacle. Prerequisite for this are sonar sensors. This feature is optional.
The robot supports a self-made Bumperduino with two MaxSonar sonar sensors and an MPX5010DP FREESCALE pressure sensor for a pressure wave hose.
The evaluation is done by an Arduino Nano, which is connected to the PinUserSwitch2 / 3 of the PCB1.3. Upon detection of an obstacle with the sonar sensors, the robot slows down and bumped gently against the obstacle where the bumper or bumper duo triggers.
The evaluation is done by an Arduino Nano, which is connected to the PinUserSwitch2 / 3 of the PCB1.3. Upon detection of an obstacle with the sonar sensors, the robot slows down and bumped gently against the obstacle where the bumper or bumper duino triggers.
The board is relatively simple. This allows them to be easily soldered together on a laboratory board. The MaxSonar sensors can be omitted and a separate solution can be connected to the Nano.
The sensor for the pressure wave hose can be omitted and only the sonar sensor is used. Another option for an approach solution is to expand the current Raindancer software.
The original Ardumower ultrasonic sensors are currently not supported.
The serial interface is used for the operation. On the mobile phone is the software Arduino Central is used (free with advertising or without advertising for a few euros). In Arduino Central, buttons can be configured with commands. The operation is via command line commands. The send line must be terminated with CR. The output is automatic shown on the console or on the mobile phone, depending on where the command was just entered.
The serial interface is used for the operation. On the mobile phone is the software Arduino Centrale is used (free with advertising or without advertising for a few euros). In Arduino Centrale, buttons can be configured with commands. The operation is via command line commands. The send line must be terminated with CR. The output is automatic shown on the console or on the mobile phone, depending on where the command was just entered.
Most commands are grouped by services. The group corresponds to the services mentioned in the software. The command following the service is then separated by a dot. Spaces are skipped and have no meaning.
This is useful when using the mobile phone, where a space is inserted after a period.
Zeile 51: Zeile 56:
  Example: pc.cm,60,30       //drives 60 cm with speed 30 (//drives... does not belong to the command)
Zeile 60: Zeile 65:
Zeile 72: Zeile 77:
Zeile 81: Zeile 86:
==Open points==
* Stability of the software in the long term. Stand 28.04.2018 Currently, the current software version mowed 63h, has traveled 59km and has rotated 8426 times
* The line tracking algorithm has been recently optimized for the rear wheel drive chassis. Due to the short distance between coil and the wheels of the original Ardumower chassis, it may be necessary to program another algorithm.
* Optimization for the original Ardumower chassis (Mowing works very well with the workaround, if necessary, play with the parameters CONF_PER_CORRECTION_ANGLE and CONF_PERIMETER_DRIVE_BACK_CM)
* Dodge objects close to the perimeter (SecondReverse2 in the BHT)
* Program one-sided accessible charging station
* Use RTC to program start at a defined time
==Other wishes==
* Integrate rain sensor
* The charging station is currently only counterclockwise approached.
* Amplify the signal of the charging station to + -20V voltage stroke
* SRF08 integration
* Integrate I2C temperature sensors
* An external start / stop button that starts or stops mowing
* Approachthe charging station with GPS. Drive 15m before the charging station on the perimeter and then drive into the charging station..
* GPS map - the mower may not recognize the signal in the middle of the lawn because the signal is too weak. You can then use GPS to see if you are on the lawn area. If you now say that the signal must be detected at least 15m away from the perimeter, you can neglect the signal within the area if the GPS signal indicates that you are on the lawn.
* GPS Map - Note where mower has already mowed. Then mow in less mowed areas if necessary.
=For minimum commissioning, the following requirements should be met=
Zeile 129: Zeile 114:
  #define ARDUMOWER_CHASSIS  false
In config.h go then to the code section, which belongs to your choice and change this section.
Zeile 162: Zeile 147:
  #define CONF_DISABLE_PERIMETER_SERVICE         false  // Disables perimeter sensor
  #define CONF_DISABLE_RTC_SERVICE true    // Disables rtc sensor
  #define CONF_DISABLE_EEPROM_SERVICE true   // Disables EEPROM requests
  #define CONF_DISABLE_BATTERY_SERVICE         true   // Disables battery sensor
  #define CONF_DISABLE_CHARGE_SERVICE true   // Disables charge system service
#define CONF_DISABLE_RAIN_SERVICE              true    // Disables rain sensor
#define CONF_DISABLE_DHT_SERVICE              true    // Disables temp sensor
#define CONF_DISABLE_GPS                      true    // Disables GPS service
  #define CONF_DISABLE_MOTOR_STALL_CHECK true   // Disables the motor stall/encoder check in closed loop control
  #define CONF_DISABLE_MOW_MOTOR         false  // Disables the mow motor
Zeile 336: Zeile 324:
 pc.a, 360,80  Rotates both wheels forward by 360 degrees with 80% speed if everything is configured correctly.
Zeile 350: Zeile 338:
Recompile and upload. Then try again.
Zeile 362: Zeile 350:
Drive a certain way in cm
 pc.cm, 60,30 drives 60cm forward with the speed of 30%
pc.cm,60,60,30,30  drives 60cm forward with the speed of 30%
Zeile 370: Zeile 358:
 turnto, 360,30  Turn the robot 360 degrees CW (clockwise)
==Mähmotor Inbetriebnahme==
==Mowmotor commissioning==
The mowing motor does not use an encoder. It is operated with a PWM of 255. The PWM of 255 is not immediately given to the engine. It ramps up the PWM from 0 to 255.
The same applies to the braking of the engine. It may happen that a motor fault is displayed when the engine is decelerating. This is because the inertia of the mowmotor disc tends to continue to rotate the motor, thus retroactively injecting a current into the motor driver that exceeds the limits such that the tri-state outputs of the driver go to high-impedance. If this happens, the error can be reset with the reset command.
Zeile 386: Zeile 374:
  t          //mow motor stop
  t          //mow motor stop
  mot.curm  //indicates the mowing motor current.
==Perimeter Inbetriebnahme==
==Perimeter Commissioning==
Prerequisite for commissioning:
Die Spulen des Roboters müssen für die Inbetreibnahme innerhalb der Perimeterschleife sein.
The spools of the robot must be within the perimeter loop for commissioning.
Die Raindancer Sender Firmware muss auf dem Sender installiert sein.
The Raindancer transmitter firmware must be installed on the transmitter.
Man kann sich die berechneten Wert der einzelnen Spulen folgendermaßen anzeigen lassen:
per.resultl für linke Spule und per.resultr für rechte Spule.
per.resultl for left coil
Am Beispiel unten kann man am BAD erkennen, dass kein gültiges Signal empfangen wurde.
and
Wichtig ist hier, dass kein BAD angezeigt wird. Die empfangene Amplitude steht hinter mag:. Die Signalqualität kann man an der Peak Signal Noise Ratio psnr sehen.
per.resultr for right coil.
The example below shows that the BAD has not received a valid signal.
It is important here that no BAD is displayed. The received amplitude is behind mag :. The signal quality can be seen on the Peak Signal Noise Ratio psnr.
  Beispiel per.resultl
Zeile 422: Zeile 412:
  mag:    5  peak @  11 :    5  peak2 @ 153 :    5  MSE:    3.286  psnr:    7.607  psnr2:    7.607  ratio:    1.000    BAD
End the output with h.
The detected perimeter amplitudes are now shown.
ML zeigt die Amplitude der linken Spule an, MR die Amplitude der rechten Spule.
ML indicates the amplitude of the left coil, MR the amplitude of the right coil.
  !03, ML: -305  MR: 331 magMax:332 magMedL%: 0 magMedR%: 102
Zeile 443: Zeile 433:
  !03, ML: -326  MR: 324 magMax:332 magMedL%: 0 magMedR%: 102
Allerdings sieht man hier, dass die Magnetude links negative ist.
However, one can see here that the magnetude on the left coil is negative.
In der Perimeterschleife muss diese positive sein.
Inside the perimeter loop, this must be positive.
  #define CONF_RIGHT_COIL_INVERSE         false
Wichtig ist, das CONF_LEFT_COIL_INVERSE und CONF_RIGHT_COIL_INVERSE so konfiguriert werden, dass per.show innerhalb der Spule positive Amplituden anzeigt.
==Konfiguration Bluetooth==
==Configure Bluetooth==
eingestellt werden.
(The perimeter outputs are extremely large.) It may be that the software faltered at this transfer rate when viewing perimeter data over BT at that baud rate.)
(Die Perimeterausgaben sind extrem umfangreich. Es kann sein, das die Software bei dieser Übertragungsrate ins Stocken gerät, wenn man sich Perimeterdaten über BT bei dieser Baudrate anzeigen läßt.)
This would be the configuration then done.
Also los:
Lets start:
==Configure Arduino Centrale ==
The software runs on an Android mobile phone or tablet.
Arduino Centrale can be downloaded from the Play Store. Another software that works is Serial Bluetooth Terminal.
Then open the button layout Configuration. Here you can set which buttons are displayed.
Nur folgendes soll angewählt sein:
Only the following should be selected:
  Show Control Button
  Show Control Button
  Show Standard Button set 1
Zeile 499: Zeile 488:
  Show Standard Button set 3
Go back and open Serial Terminal Settings
Set Terminal View Character Limit to 10000
  Select CR
  Select NL
Als erstes muss nun das BT Modul mit dem Handy gekoppelt werden.
First, the BT module must now be paired to work with the mobile phone.
Das heißt am Handy BT Aktivieren.
That means on the phone enable BT.
Dann in das BT Menue am Handy gehen und nach neuen Geräten suchen.
Then go to the BT menu on the phone and look for new devices.
Dort sollte dann eine neues Gerät auftauchen. Dieses Geräte auswählen und paaren bzw koppeln.
There should then appear a new device. Select this device and pair.
Es kommt zu einer Passwortabfrage die 1234 ist oder auch 0000
There is a password query which is 1234 or 0000
Thereafter, the module is included in the device list
Jetzt in Arduino Cnetral im Menü auf connect to Device gehen und das BT des Robbis  klicken.
Now in the menu of Arduino Centrale go to connect to device and click the BT of the mower.
If everything was successful, BT connect should be displayed at the top right.
In Arduino Central können unter dem Menüpunkt Standard Button Setup Befehle hinterlegt werden.
In Arduino Centrale commands can be stored under the menu item Standard Button Setup.
Aktuell habe ich bei mir folgende Befehle hinterlegt:
Currently I have deposited the following commands with me:
  Button 1 Text: Manual Command: M
  Button 2 Text: Auto  Command: A
Zeile 531: Zeile 520:
==Erste Testfahrt==
== First test drive ==
=TUNE UP =
=TUNE UP =
== Configure the bumpers on the bumper connectors ==
  #define CONF_RIGHT_BUMPER_LOW_ACTIVE   true    // right bumper is activated when pin is low
''If you want to switch off the pull-up resistors, the lines must be changed as follows''
==Charge Service==
==Charge Service==
Daher sollte EF1 5A betragen.
Annotation:
Therefore, EF1 should be 5A.
[[The following describes how to load the robot.]]
'''Independent driving in the charging station'''
When the robot moves into the charging station, the charging relay is switched off. At this time, only the voltage of the charging station is at the contacts.
If the robot has detected this, it stops, waits two seconds and checks the charging voltage again. If this is OK, it moves 3cm forward, 3cm backwards and again 2cm forward.
This serves to optimize the connection to the charging contacts (which are currently designed as sliding contacts). Then the relay is switched on and the charging voltage checked again.
(This behavior can easily be reprogrammed in the BHT.) The relay remains energized and thus the battery is connected to the charger until the robot is commanded to go to an area or the robot is switched to manual mode or switched to auto mode.
'''Use without charging station'''
To load the robot it should be in manual mode (enter command M). Then you can use charge.relay,1 to switch on the relay and with charge.relay,0 to switch off the relay. The relay automatically turns off when the Auto mode is activated. '''The relay only switches on if the charging voltage is applied to the charging contacts!'''.
Another possibility is to connect the charging contacts when switched off and then turn on the robot. The robot then goes into auto mode and turns on the Behavior Charging Station. He now thinks he is in the charging station.
'''Put in the charging station'''
[[Manuelles Testen:]]
[[Manual testing:]]
Enter the command:
Enable relay:
Disable relay:
[[Testing in the off state via the console:]]
Turn on the robot and connect USB. Wait until software has started up.
Ladekontakte verbinden.
Connect charging contacts.
Open the serial console. The DUE restarts. The relay should be energized and the console output at boot should show "Charging station detected".
The robot has now switched to the Chargingbehaviour.
==Watchdog==
==Watchdog==
The watchdog is solely for safety.
If the software hangs, the watchdog should prevent the robot from running unchecked.
The watchdog is hardware implemented in the DUE. It is activated in the config.h with:
If watchdogReset (); is not called within 3 seconds  (because the software hangs somewhere), the DUE is restarted, stopped the engines and the software goes into manual mode.
Annotation:
Since the variables of the firmware are reinitialized during the reboot, it is difficult to find out what the cause of the error is.
The Mower simply stops, and one wonders when opening the BT connection, that everything is fine and no error is issued - except that the software is in manual mode.
== Undervoltage Shutdown ==
The undervoltage shutdown is used to prevent the battery from falling below a certain voltage and then deeply discharged. The implementation of the undervoltage shutdown is implemented in the battery service.
Prerequisite is, that the jumper 8 UV shutdown on PCB 1.3 is set to Auto. If you then put voltage on the board, this gets no electricity first. Therefore, when switching on the voltage, the UV shutdown must be bridged with the P20 button. Then the PCB1.3 gets voltage. This button should be held for 4 seconds. Then the software takes control of the UV shutdown. The P20 button must then be open again, otherwise the software can not switch off the voltage.
If the battery voltage falls below this voltage for one minute, the voltage to PCB1.3 and the motors will be cut off.
The entire PCB1.3 is then dark.
==I2C Bus==
==I2C Bus==
Zeile 754: Zeile 697:
==RTC==
==RTC==
The RTC module is currently not used. It is intended to use this later for a time mowing start.
However, the RTC module can already be programmed and tested.
Zeile 768: Zeile 711:
==EEPROM==
==EEPROM==
Zeile 785: Zeile 728:
With the command
== Slow down the speed at the perimeter ==
Die Werte  magMedL%: 73 magMedR%: 87 zeigen hier die gemessene Prozentzahl der Spulen an. Hiernach dann CONF_NEAR_PER_UPPER_THRESHOLD und CONF_NEAR_PER_LOWER_THRESHOLD einstellen. Es sollten mehrere Versuche zur Bestimmung durchgeführt werden. Besser etwas früher langsamer werden, als zu spät. Der Unterschied zwischen High und Low wurde eingeführt, da die Spulen nicht den gleiche Wert haben, z.B. wenn der Mower schräg oder fast parallel zum Perimeter fährt.
The values magMedL%: 73 magMedR%: 87 indicate here the measured percentage of the coils 20cm before the  perimeter wire. Use this percentage as starting point to set CONF_NEAR_PER_UPPER_THRESHOLD and CONF_NEAR_PER_LOWER_THRESHOLD. Several tests should be carried out for the determination. Better to slow down a little earlier than to slow down too late. The difference between UPPER and LOWER has been introduced because the coils do not have always the same value, e.g. when the Mower is running obliquely or almost parallel to the perimeter.
The calculation is stored in the function '' 'bool TPerimeterThread :: isNearPerimeter ()' '' in the file perimeter.cpp.
==Mähmotorstrom einstellen==
== Set mower motor current ==
Forumseintrag:
Forum Posts:
angezeigt.
== Slow down when mower engine is loaded ==
Attention, the motor drivers deliver an accurate current measurement only from 1A on (according to data sheet 0.5A).
That Values where the current is displayed under 1A are inaccurate and should not be used.
The accuracy is according to data sheet at a current of over 0.5A + -20%.
==Spiralfahrt==
            bb.flagCruiseSpiral = true;
(a)  Eine Spirale wird aktiviert, wenn bb.mowMotorSensor.motorUnderHeavyLoad() true zurückgibt und die letzten 60 Sekunden keine Spirale gefahren wurde. Die Berechnung in  bb.mowMotorSensor.checkIfUnderLoad() wird durch die die Konstante
beeinflusst. Zum bestimmen ob der Motor under heavy load ist, wird eine Hysterese verwendet. Sobald die  Mähmotor Wattzahl über CONF_MOW_MOT_UNDER_HEAVY_LOAD_ON    geht, gibt bb.mowMotorSensor.checkIfUnderHeavyLoad() true zurück. Doch erst wenn die Wattzahl wieder unter CONF_MOW_MOT_UNDER_HEAVY_LOAD_OFF  geht wird false zurückgegeben.
==Perimeter Tracking==
Here, the perimeter tracking algorithm is explained, with the aim of providing enough information to be optimized by the user on its chassis. The choice fell on this algorithm, since it is independent of the perimeter amplitude. Furthermore, the algorithm is extremely stable and is to be diverted from its intention to follow the perimeter. [https://www.youtube.com/watch?v=RdufyzkYSPU '' 'Video Example' '']
The perimeter tracking algorithm uses a one bounce algorithm. The algorithm move off counterclockwise on the perimeter. The right outer coil bounce always against the perimeter from the outside. When it hits the perimeter, the coil is first repelled by the perimeter. Thereafter, the coil moves in an arc towards the perimeter. [https://www.youtube.com/watch?v=Y3wxURV0qtw '' 'Video Example' '']
[[Datei:OneBounce.png]]
The algorithm is in the file: bGotoAreaX.h class: TlineFollow implemented.
The following diagram shows the "if" queries in a different chronological order for a better explanation than they actually are in the program code. Therefore, do not be confused when looking at the program code.
Ablauf:
Procedure:
The right coil is always outside the perimeter.
If this exceeds the perimeter inwards, an aggressive rotation is first executed clockwise with:
Zeile 950: Zeile 838:
Zeile 958: Zeile 846:
When the coil is now turned out, the robot moves a shallow counter clockwise curve  until it reaches the perimeter.
For the calculation of the curve, an integral is used, which can be controlled by the factor Ki.
(Note: The integral is set to 0 as soon as the coil crosses the perimeter.)
  double Output = integral;
  bb.motor.L->setSpeed((bb.cruiseSpeed + Output));  // note: output is negative
Zeile 992: Zeile 880:
Zeile 1.002: Zeile 890:
Testen des Algorithmus:
Testing the algorithm:
Place the robot on the perimeter so that the right coil is on the outside and the left coil on the inside. Start the perimeter tracking with the command.
Der Befehl
The command
stops the test.
With the command
set.lfki, 1.1
== Fast return ==
On the way back to the charging station, it may happen that the Mower drives at one point onto the perimeter so that it has to drive the entire perimeter wire to the charging station. To shorten this way, there is the fast return.
The user has to lay the perimeter cable so that it results in a square. This quadrilateral is then recognized by the robot during perimeter tracking. When he recognizes the square, he turns 90 degrees from the perimeter into the interior, and moves to the other side of the lawn. When he discovers the perimeter cable, he picks up the perimeter tracking again.
==Schnelle Rückkehr==
Zeile 1.031: Zeile 923:
   File:Raindancer FastReturn.png |  Example, how I lay down my squares
Die entsprechenden Winkel und maximal Distanzen muss man dann im Code in der Klasse: class TfindTriangle anpassen.
The corresponding angles and maximum distances must then be adapted in the code in class: class TfindTriangle.
Below Ishow slightly thinned class to get a better overview. The lines errorHandler.setInfoNoLog (..) are the output if the command bht.tri has been activated. These were listed here to better interpret the issue.
Zeile 1.062: Zeile 954:
Abfrage der States
Query the States
Zeile 1.079: Zeile 971:
In case 1 wird ständig überprüft, ob eine bestimmte Strecke nach der Linkskurve überschritten wurde. Im Beispiel 55cm. Wenn ja, ist das zu weit und es wird wieder zurück in den case 0 gesprungen, da es nicht sein kann, das das Dreieck so lang ist. Wenn innerhalb der Strecke von 55cm dann ein  Winkel > 50 gefunden wurde, wird in den case 2 gesprungen. Ein positiver Winkel bedeutet eine Rechtskurve/-drehung.
Zeile 1.098: Zeile 990:
Zeile 1.117: Zeile 1.009:
Zeile 1.132: Zeile 1.024:
== Mowing zones between adjacent surfaces ==
Siehe Bild:
See image:
Zeile 1.149: Zeile 1.041:
''(In the picture above, it is not normally necessary to set up mowing zones, as the robot covers relatively well all areas of the lawn by the algorithm.)''
area,x    // where x is the path to be traveled in m.
== Laying the Perimeter Cable at Corners ==
The Mower determines in which direction he turns on the perimter on the basis of the coil that was pulled out first. Therefore it is important not to lay the corners at 90 degrees.
For example, if the Mower, with the right spool, moves close parallel to the perimeter and then drives out at the corner, the right spool should also be the first to leave the perimeter.
Zeile 1.182: Zeile 1.069:
=Perimeter Sender=
==Temperature Sensor==
The temperature sensors DHT11 / DHT21 / DHT22 / AM2301 are supported. Currently only the sensor DHT22 was tested.
The temperature sensor is connected to the designated port of the PCB1.3.
#define DHTTYPE DHT22
temp.show
In manual mode, the sensor is read out directly. Temperature, humidity and the last temperature stored in the service are displayed.
In auto mode, only the temperature stored in the service is displayed. The temperature is updated when the mower drives over the perimeter wire and comes to a stop and time has passed at least 20 seconds since the last measurement.
==Rain Sensor==
When the robot mows in AUTO mode and it starts to rain, the robot returns to the charging station.
The rain sensor is connected to the designated port of PCB1.3.
The sensitivity of the rain sensor is set on the rain sensor with the potentiometer.
rain.show
==Shutdown Service==
When the shutdown service is activated, it shuts off the power via the undervoltage protection.
If a Raspberry PI is connected to the USB port,
can be set.
Then the software waits 50 seconds for shutdown.
Every second, $PwrOff and a countdown are sent to the PI so that it can shut down.
With the command:
  poweroff
the shutdown can be activated via the user interface or from the PI.
The shutdown service is also used by the battery service and the temperature service to shut down.
Thus, the PI is informed that it should shut down if the battery voltage is too low or the temperature too high.
==GPS Service==
The GPS module is connected to the dedicated connector on PCB1.3. The GPS module periodically sends data to PCB1.3.
If no data is received, please read the following article. It may be that RX3 and TX3 on the PCB1.3 were wired incorrectly.
===Send to the Raindancer Controlcenter===
set.cco, 1
set.cco,0
By default, the GPS module sends multiple records in a 1 second interval. These records are not all needed and generate an overhead.
Only the record: $GPRMC for NEO-6M and $GNRMC for NEO-M8N are needed.
Therefore, there is the possibility to configure the module when starting the Raindancer firmware so that it sends only the required record and this only in a 3 second cycle.
For this the following parameter is set:
=== Enable internal calculation ===
Again #define CONF_INIT_GPS_WITH_UBLOX should be true.
To activate the internal calculation CONF_DEACTIVATE_GPS_CALCULATION  must be set.
For the NEO-6M module, the record: $GPRMC is used. The NEO-M8N uses the record $GNRMC.
Therefore, the following lines must be commented in or out depending on the module used:
With
gps.show
Each column belongs to a polygon point. You can at https://www.google.com/maps enter a point in the search: 54.08728,10.448400. Then you can see where this coordinate is. So you can see point by point how the polygon is constructed.
It is important that the number of columns is defined correctly with CONF_NUMBER_OF_POLYGON_POINTS. You can enter 3 to N coordinate points. However, I suggest you use no more than 8 points to make the calculation time as low as possible
was introduced. This means that if the amplitude of the perimeter exceeds this value, the perimeter signal will be used in any case and will not be overwritten by the GPS signal, even if the mower is in the GPS range.
The value 300 must be set according to your own requirements..
[[File:warning.png]]'''Safety Note: If the perimeter signal fails and the GPS range exceeds the perimeter, the mower will leave the perimeter area'''
=Perimeter Sender=
The original Ardumower transmitter hardware is used. The software has been changed slightly. A 128 bit signal is sent.
The following perimeter signal is sent:
*1. 12V vorhanden
*1. 12V available
*2. 5V vorhanden
*2. 5V available
*3. Green when the interrupt which produces the signal is running (red LED not available because of wrong pin at Nano). Off when charging.
*4. Green when a current flows through the perimeter, red when no current is flowing (perimeter interrupted) or very little current because of high protective resistor. Off when charging.
*5. Yellow the robot is charging. Perimeter signal is switched off. LED 2 and 4 off.
'''If the transmitter is on and the robot does not return to the charging station after twelve hours, the transmitter will turn off the signal.''' Then either reboot the transmitter or load the robot into the charging station.
=Charging Station =
If no charging station is used,
should be set. Then the Mower drives at low battery voltage to the perimeter and stops.
==Head charging station==
With the command
gohome
tpt
area,0
==Through  Charging Station==
With the command
gohome
tpt
  area,10
The Mower then travels 10m along the perimeter wire and then starts mowing. 10m can be exchanged against any distance.
=Troubleshooting=
=Troubleshooting=
==Mower bleibt stehen==
== Mower stops ==
[[Problem:]]
[[Problem:]]
Mower stopped, cause was probably the transmitter. On the transmitter just lights still the two left LEDs. Transmitter turned and on again, 4 LEDs back to green and then it works again.
[[Lösungsvorschlag:]]
[[Solution:]]
The third green light from the left indicates whether the transmitter Interrupt is running in the Nano.
Möglichkeit a)
Possibility A)
The transmitter is on for more than 12 hours without the robot returning to the station. Then the transmitter turns off the perimeter signal.
Möglichkeit b)
Possibility b)
Since this was not on, the nano seems to have hung up. If that happens again, I would swap the China Nano for an original Arduino Nano. Since the software has been running for me for a year, I do not assume that the software is the cause. I had used cheap nanos before. They were not really frequency stable with me, which is necessary for the transmitter however. Now I have an original in it.
==I got the message: Out: READ und In: CMD==
  Out: READ
  Out: READ
Zeile 1.225: Zeile 1.302:
  Out: READ
  Out: READ
[[Suggested solution:]]
In the Arduino Centrale Settings "Read Command -> Enable Read Command" is activated
Aktuelle Version vom 9. August 2020, 13:00 Uhr
This documentation is for firmware version 2.x.x.
Github Download
Overview
Example: clc.enc
Which modes will start when:
  • PCB1.3 with Arduino DUE
  • BT module
  • 24V power supply
Optional can be used
  • RTC with EEPROM
Console Speed:
has to be changed to:
  #define PWM_FREQUENCY 3900
  #define TC_FREQUENCY 3900
Errorhandling
error     //show errormessage
show.hist   //show history
A
Commissioning of the motors
Enter the command:
Commissioning the encoder
Enter the command
clc.mt, 1,150
to make the left wheel turn.
Enter then
clc.mt, 2,150
Enter:
then
clc.v, s stop engine
then
Drive a certain way in cm
Mowmotor commissioning
z          //mow motor start
t          //mow motor stop
Perimeter Commissioning
per.resultl for left coil
and
per.resultr for right coil.
Beispiel per.resultl
End the output with h.
Configure Bluetooth
Configure Arduino Centrale
Show Control Button
Show Standard Button set 1
Show Standard Button set 2
Show Standard Button set 3
Select CR
Select NL
First test drive
Annotation:
Therefore, EF1 should be 5A.
Use without charging station
Put in the charging station
Manual testing:
Enter the command:
Enable relay:
Disable relay:
Undervoltage Shutdown
With the command
Set mower motor current
double Output = integral;
The command
stops the test.
With the command
set.lfki, 1.1
Fast return
Query the States
   return BH_RUNNING;
See image:
Temperature Sensor
#define DHTTYPE DHT22
temp.show
Rain Sensor
rain.show
Shutdown Service
GPS Service
set.cco, 1
set.cco,0
Enable internal calculation
With
gps.show
  • 1. 12V available
  • 2. 5V available
Charging Station
Head charging station
With the command
gohome
tpt
area,0
Through Charging Station
With the command
gohome
tpt
Mower stops
Out: READ
Out: READ
Out: READ
Out: READ