(→Coil) |
(→Perimeter) |
| (146 dazwischenliegende Versionen von 3 Benutzern werden nicht angezeigt) | |||
=Abstract= | =Abstract= | ||
| − | A perimeter wire (or buried wire fence, BWF) is like a 'virtual fence': it stopps the robot when it reaches its boundaries. A perimeter is not always necessary for all surroundings | + | A perimeter wire (or buried wire fence, BWF) is like a 'virtual fence': it stopps the robot when it reaches its boundaries. A perimeter is not always necessary for all surroundings. |
Principle idea: You will install a perimeter loop (a wire) in your garden through which a signal is sent and this signal is detected by the robot. So, you'll need: a sender (to transmit the on the wire) and a receiver (to detect the signal in the robot). | Principle idea: You will install a perimeter loop (a wire) in your garden through which a signal is sent and this signal is detected by the robot. So, you'll need: a sender (to transmit the on the wire) and a receiver (to detect the signal in the robot). | ||
| − | How is the signal detected? The signal is detected by one | + | How is the signal detected? The signal is detected by one receiver coils. The closer the distance between coil and perimeter loop, the higher the signal strength. Also, something interesting happens when the robot crosses the perimeter loop: the signal changes its polarity, that means positive and negative voltages reverse each other. |
File: Ardumower_perimeter.jpg | Perimeter wire | File: Ardumower_perimeter.jpg | Perimeter wire | ||
File: Perimeter_signal_strength.jpg | Signal strength | File: Perimeter_signal_strength.jpg | Signal strength | ||
File: Perimeter_gradient.png | Perimeter gradient | File: Perimeter_gradient.png | Perimeter gradient | ||
File: Perimeter_excluding_objects.png | Excluding objects | File: Perimeter_excluding_objects.png | Excluding objects | ||
| + | File: Perimeter_divide.png | Dividing areas | ||
| − | + | =Perimeter= | |
| − | =Perimeter | + | |
[[Image:Yt-brand-standard-logo-95x40.png|thumb|180px|https://www.youtube.com/watch?v=NIer_kITelc&feature=youtu.be]] | [[Image:Yt-brand-standard-logo-95x40.png|thumb|180px|https://www.youtube.com/watch?v=NIer_kITelc&feature=youtu.be]] | ||
| Zeile 26: | Zeile 20: | ||
This is the new version of the perimeter sender and receiver (that can be purchased via the [https://www.marotronics.de/index.php?k=7 shop] [[File: shopping.png|link=https://www.marotronics.de/index.php?k=7]]). | This is the new version of the perimeter sender and receiver (that can be purchased via the [https://www.marotronics.de/index.php?k=7 shop] [[File: shopping.png|link=https://www.marotronics.de/index.php?k=7]]). | ||
| − | + | The perimeter sender outputs a digital code sequence (a 'pseudo-noise' code), and the receiver will detect that code using a software-based digital matched filter. Depending on wheter the match result peak is positive or negative, the robot is inside or outside of the perimeter wire. | |
| − | + | Sender principle: | |
| − | # | + | # Sender PCB generates an output signal using an Arduino Nano (about 3 Khz) |
| − | # | + | # The generated signal is amplified using a motor driver (MC33926), the motor driver output is connected to the perimeter wire (instead of a motor) |
| − | The images below explain why the polarity of the received coil signal changes between inside and outside of the perimeter wire. The image shows the direction of the electric flux lines sent out from the perimeter wire and how they hit the coil for both inside and outside position. | + | Receiver principle: |
| + | # A coil receives the signal | ||
| + | # The signal is amplified using an operational amplifier (LM386) | ||
| + | # The Arduino Mega samples the signal using its analog-to-digital converter (ADC) at 9615 Hz | ||
| + | # The digital signal is filtered using a digital filter (matched filter algorithmn) | ||
| + | # The matched filter output is evaluated (for perimeter inside/ouside detection, tracking etc.) | ||
| + | The images below explain why the polarity of the received coil signal changes between inside and outside of the perimeter wire. The image shows the direction of the electric flux lines sent out from the perimeter wire and how they hit the coil for both inside and outside position. | ||
| + | For a better understanding of the perimeter filter, see the [http://www.grauonline.de/alexwww/ardumower/filter/filter.html Matched filter simulation]. For more details about the filter, also see the [https://www.youtube.com/watch?v=NIer_kITelc Matched filter video]. Using a simple symmetric signal (which looks equal on positive and negative side of the zero point), you cannot differentiate between an 'inside perimeter' and 'outside perimeter' signal. When the mower is traversing the perimeter loop, the signal polarity changes (positive becomes negative and negative becomes positive). We want to detect this polarity change of the signal. Using an unsymmetrical signal, you can do this. You can see the difference in the simulator. The default signal (slider 'example signal') is a symmetric signal - press the 'Invert' button to invert the signal (change its polarity). In the correlation result (graph 'Matched filter') the polarity can not be detected. Now use an asymmetrical signal ('pseudonoise5_pw'). Press again 'Invert' to change signal polarity. Now you can see polarity of the signal in the filter output (graph 'Matched filter'). It's the sign of the peak (positive or negative sign). | ||
File: Ardumower_perimeter2.jpg| Inside/outside detection using polarity change | File: Ardumower_perimeter2.jpg| Inside/outside detection using polarity change | ||
File: Fluxdirections.png| Flux directions | File: Fluxdirections.png| Flux directions | ||
File: Perimeter_signal_steps.png | Perimeter signal at sender and receiver coil | File: Perimeter_signal_steps.png | Perimeter signal at sender and receiver coil | ||
| − | + | File: Matched_filter_principle.png| Matched filter | |
| − | + | File: Perimeter_signal_good_bad.png|What makes a good/bad signal | |
==Sender== | ==Sender== | ||
| − | + | [[Image:Ina169_marotronics.jpg|thumb|200px| Note for Marotronics INA169: Short pads for 5A operation]] | |
| − | + | [[File: Ardumower_perimeter_overview.jpg|600px]] | |
| − | File: | + | |
| − | We use a motor driver as output amplifier and an Arduino Nano to generate the signal. The motor driver is driven by 3.2 Khz (two pulse widths 4808 Hz and 2404 Hz | + | We use a motor driver as output amplifier and an Arduino Nano to generate the signal. The motor driver is driven by 3.2 Khz (two pulse widths 4808 Hz and 2404 Hz). We use a motor driver with integrated current limiting and thermal switch-off (e.g. MC33926). |
| − | + | [[File:warning.png]] The perimeter wire length should be in the range 20m - 450m and must be at least 5 Ohm and not more than 12 Ohm. The maximum perimeter area is 1000 m2. | |
| − | + | MC33926 wiring: The perimeter wire is connected between MC33926 M1OUT1 and M1OUT2. | |
| − | + | * [https://www.marotronics.de/Perimeter-Sender-Board-Prototyp-mit-Platinen-Zubehoer sender PCB in the shop] | |
| − | [ | + | * [https://github.com/Ardumower/ardumower/blob/master/pcb/Produzierte_Platinen/sender_v2_geschlossen/Perimeter%20sender%20v2.pdf sender PCB schematics] |
| + | * [https://github.com/Ardumower/ardumower/tree/master/pcb/Produzierte_Platinen/sender_v2_geschlossen/Platinenbilder sender PCB pictures] | ||
| − | ===Sender | + | ===Sender software=== |
| − | + | <b>NOTE</b>: If you have never worked with Arduino before or if your Arduino Nano does not seem to respond, please read our <b>[http://wiki.ardumower.de/index.php?title=Arduino_first_steps 'Arduino first steps' introduction]</b>. | |
| − | + | <b>Download</b>: You can find the sender code in the 'sender' folder of the [http://wiki.ardumower.de/index.php?title=Ardumower_PCB#Download_and_flash_Arduino_code Ardumower Download] | |
| − | + | [[File:warning.png]] Note: Always verify that the pin configuration in your Arduino code (sender.ino) matches your actual circuit! | |
| − | ===Sender | + | ===Sender power control=== |
| − | + | [[File:warning.png]] The perimeter wire resistance (R) must be at least 5 Ohm and not more than 12 Ohm. Ideally, a 12 ohms (50W) power resistor is placed in series with the perimeter wire, so you get a total resistance of the perimeter wire at 12-15 ohms. | |
| − | + | To change the power (current/voltage) of the sender, proceed like this: | |
| − | + | The motor driver output voltage can be changed between 6.5-12V via the potentiometer on the DC/DC converter. Adjust the potentiometer so that not more than 1 Ampere current flows. | |
| − | + | Example: | |
| + | Your perimeter wire resistance (R): 12 Ohm | ||
| + | Your adjusted voltage at the DC/DC converter: 8 Volt | ||
| − | + | The consumed current and power is then: | |
| + | Current: I = U / R = 8 Volt / 12 Ohm => 0.7 Ampere | ||
| + | Power: P = U * I = 8 Volt * 0.7 Ampere => 5.6 Watt | ||
| − | + | Power resistor: If your perimeter wire resistance (R) is below 5 Ohms, you will not be able to further reduce voltage below 6.5v (otherwise the motor driver will not work properly). Then you have to increase the perimeter wire resistance (R) by using a power resistor in series with your perimeter wire. Important: your power resistor must be suitable for the power! In the example above usng a 12 Ohm power resistor, it should be a 10 Watt type. | |
===Sender automatic standby=== | ===Sender automatic standby=== | ||
| − | The sender can be switched off during the time the robot is in the charging station. To detect the robot, a current sensor ( | + | The sender can be switched off during the time the robot is in the charging station. To detect the robot, a current sensor (INA169, 5A) is connected between the charger and the charging pins. |
===Sender diagnostics=== | ===Sender diagnostics=== | ||
| Zeile 189: | Zeile 93: | ||
* blinking: robot is charging and perimeter will be switched OFF (energy saving) | * blinking: robot is charging and perimeter will be switched OFF (energy saving) | ||
| − | + | To find errors (or to better understand the sender), open the serial console via Arduino IDE (CTRL+SHIFT+M) at 19200 baud. Now you can see the possible states (robot in charging station, robot outside charging station etc.): | |
| − | File: | + | File:Perimeter_sender_console.png | Perimeter sender console output |
| − | + | ==Receiver== | |
| − | + | [[File:Perimeter_v2_receiver_circuit.png |400px]] | |
| − | For receiving the signal, we use a coil (100 mH or 150 mH) in upright position (centered at front in robot) | + | For receiving the signal, we use a coil (100 mH or 150 mH) in upright position (centered at front in robot) connected to an LM386 operational amplifier (to amplify the received signal). When using the [https://www.marotronics.de/Schleifenempfaenger-Kit-perimeter-receiver-Kit LM386 module], capacitor C3 on the LM386 module should be bypassed (which is needed so that the LM386 generates a signal between 0..5V and not the default range -5V..+5V). The LM386 output pin should be connected to an analog Arduino pin ('pinPerimeterLeft'). |
| − | File: | + | File: Ardumower_chassis_components.png | Perimeter coil position |
File: Ardumower_coil_position.jpg | One centered, upright coil | File: Ardumower_coil_position.jpg | One centered, upright coil | ||
File: Ardumower_lm386_circuit.png | LM386 module schematics | File: Ardumower_lm386_circuit.png | LM386 module schematics | ||
| + | File: Dcdc_noise.jpg | NOTE: Keep away coil/pre-amplifier from DC/DC converters | ||
File: Tire_coil_distance.jpg | Tire-coil distance effecting rotation angle | File: Tire_coil_distance.jpg | Tire-coil distance effecting rotation angle | ||
| − | + | [https://www.marotronics.de/Schleifenempfaenger-Kit-perimeter-receiver-Kit You can get the receiver kit in the shop] | |
'''NOTE''': It's recommended to directly mount the coil on the amplifier module. This ensures the 'small signal' of the coil is not distorted by other components (motors, DC/DC converters etc.). | '''NOTE''': It's recommended to directly mount the coil on the amplifier module. This ensures the 'small signal' of the coil is not distorted by other components (motors, DC/DC converters etc.). | ||
| − | ''' | + | '''Note''': Leave out capacitor 4.7nF in latest software versions ('using differential signal'). |
| − | + | ===Settings=== | |
| − | <gallery> | + | <gallery> |
| − | + | File:Cheat_sheet.png | Perimeter settings | |
| − | ===Coil=== | + | At first, activate the perimeter in the Ardumower software (pfodApp->Options->Perimeter Use: YES). It is recommended to keep the default perimeter settings. |
| + | The perimeter settings are: | ||
| + | * Timed-out if below smag (timedOutIfBelowSmag) - default setting: 300 | If smag below this value, sender is considered as off (perimeter timeout appears) | ||
| + | * Timeout (s) if not inside (timeOutSecIfNotInside) - default setting: 8 | ||
| + | ===Coil/amplifier-to-motor distances=== | ||
| + | Ensure all minimum distances to the following components: | ||
| + | * Coil to gear motor: > 15cm | ||
| + | * Coil to mower motor: > 10cm | ||
| + | * Coil to DC/DC converter: > 10cm | ||
| − | File: | + | File: Dcdc_noise.jpg | NOTE: Keep away coil/pre-amplifier from DC/DC converters and motors! |
| − | + | </gallery> | |
| − | File: | + | ===Signal measurements=== |
| − | File: | + | The sender / coil / LM386 amplifier outputs should look like this: (for more details about the signal, see section signal above) |
| − | File: | + | <gallery> |
| − | File: | + | File: Perimeter_signal_steps.png | Perimeter signal at sender, receiver coil, and LM386 (principle) |
| + | File: coil_signal_without_capacitor.png | sender signal, coil signal (5V sender, 5 ohm loop - blue: perimeter, yellow: coil, gray: LM386 amplifier out) | ||
| + | File: Perimeter2_sender_open.jpg| Sender signal (6.5V, open perimeter) | ||
| + | File: Lm_output_dc_noise.jpg | LM386 output, with DC noise | ||
| Zeile 274: | Zeile 185: | ||
| − | File: | + | File: Perimeter_snr.png | Signal-to-noise ratio (SNR) |
| − | File: | + | File: Perimeter_signal_38khz.png | signal, filter result, LP filter result, inside/outside, counter, on/off, quality |
File: Perimeter_plot_moving_from_inside_to_outside.png | Moving from inside to outside | File: Perimeter_plot_moving_from_inside_to_outside.png | Moving from inside to outside | ||
| − | File: | + | File: Perimeter_plot_signal_strength.png |
File: Perimeter_v2_plot_new.png | File: Perimeter_v2_plot_new.png | ||
File: Ardumower_perimeter2_test.jpg | File: Ardumower_perimeter2_test.jpg | ||
| Zeile 288: | Zeile 199: | ||
- this is used for <b>perimeter tracking</b> | - this is used for <b>perimeter tracking</b> | ||
smag: filter result, low-pass filtered, without sign (smooth mag) - this is used for <b>'sender-off' detection</b> | smag: filter result, low-pass filtered, without sign (smooth mag) - this is used for <b>'sender-off' detection</b> | ||
| + | The threshold can bet set via pfodApp (Settings->Perimeter->Timed-out if below smag) | ||
in: binary result, low-pass filtered: inside (1) oder outside (0) - this is used for <b>perimeter boundary detection</b> | in: binary result, low-pass filtered: inside (1) oder outside (0) - this is used for <b>perimeter boundary detection</b> | ||
| + | If the robot is not inisde for a certain time, it will go into error. The threshold can bet set via pfodApp | ||
| + | (Settings->Perimeter->Timeout (s) if not inside) | ||
cnt: number of "inside-outside" transitions (counter) | cnt: number of "inside-outside" transitions (counter) | ||
| − | on: perimeter sender active (1) or inactive (0) | + | on: perimeter sender active, robot is inside and smag is high enough (1) or inactive/outside/smag too low (0) |
| − | qty: <b>signal quality</b> ( | + | qty: <b>signal quality</b> (how distinguisable inside and outside were in filter result |
| − | + | computes ratio: match score with template signal / match score with inverse template signal | |
| + | 1.0 means poor quality, you should get 1.5 or higher) | ||
The 'mag' plot should be clear (without spikes): Inside the perimeter loop, the signal should be a clear negative curve, outside it should be a clear positive curve. If your 'mag' curve is not clear (and has spikes), try to troubleshoot/optimize: | The 'mag' plot should be clear (without spikes): Inside the perimeter loop, the signal should be a clear negative curve, outside it should be a clear positive curve. If your 'mag' curve is not clear (and has spikes), try to troubleshoot/optimize: | ||
* Verify, your coil is connected correctly at 'pinPerimeterLeft' (you still may get a poor signal when connected at a wrong Arduino pin!) | * Verify, your coil is connected correctly at 'pinPerimeterLeft' (you still may get a poor signal when connected at a wrong Arduino pin!) | ||
| + | * Decrease the threshold for a smag timeout via 'pfodApp->Options->Perimeter->Timed-out if below smag' | ||
* Reverse coil if the in/out is inverted or reverse the perimeter wire | * Reverse coil if the in/out is inverted or reverse the perimeter wire | ||
* Minimize cable length between coil and LM386-pre-amplifier (directly mount coil onto pre-amplifier) | * Minimize cable length between coil and LM386-pre-amplifier (directly mount coil onto pre-amplifier) | ||
* Increase distance between coil and mower motor/DC converter (move away coil 30cm or more from any motors or DC converters) | * Increase distance between coil and mower motor/DC converter (move away coil 30cm or more from any motors or DC converters) | ||
| − | * Add some magnetic shield (e.g. your battery) between coil and motors/DC converter | + | * Add some magnetic shield (e.g. your battery) between coil and motors/DC converter |
| − | == | + | ==Broken perimeter wire== |
| + | Once in a while your perimeter wire may get broken, and your perimeter loop resistance will probably increase to a few Megaohms (MOhm). If that is the case, you can find the location of the break like this: | ||
| − | + | # Using a metal plate, plug one wire of the perimeter sender output into earth ground (the other wire of the sender output is still connected to the perimeter wire) | |
| + | # Optional: increase your sender output voltage to 20 Volts (NOTE: the MC33926 driver can NOT operate higher than 28v, and your sender Arduino Nano may not operate higher than 20v) | ||
| + | # Method 1 (using two LM386 amplifiers and earphone): Connect 1st LM386 amplifier (NOTE: do NOT remove capacitor C3!) signal output to a 2nd LM386 input. Connect 2nd LM386 output to an earphone. | ||
| + | # Method 2 (using one LM386 amplifier and a PC): Connect the LM386 amplifier (NOTE: do NOT remove capacitor C3!) signal output (signal and GND) to your PC's microphone input, launch the [http://www.grauonline.de/alexwww/ardumower/oscilloscope/oscilloscope.html web oscilloscope], and switch into frequency view (choose visualization 'frequency spectrum') | ||
| + | # Turn on the perimeter sender - while traversing the perimeter wire, you will notice a peak frequency of 3.2 Khz in the Web oscilloscope | ||
| + | # Now start at the side of the perimeter wire (the side that is still connected to the perimeter wire), and walk along the perimeter wire - the peak frequency of 3.2 Khz should always be there (and hearable) | ||
| + | # At the location where the wire is broken, the 3.2 Khz frequency is gone (and no longer hearable)! [https://youtu.be/J6X_dktw4ZE Demonstration video] | ||
| − | + | <gallery> | |
| − | + | File: Peri_broken2.jpg | Plug one wire into ground (earth) | |
| − | + | File: Peri_broken4.jpg | Method 1: Connect 1st LM386 amplifier output to 2nd LM386 input, 2nd output to earphone | |
| − | + | File: Peri_broken1.jpg | Method 2: Connect LM386 amplifier output to your PC's microphone input | |
| − | + | File: Peri_broken3.jpg | Method 2: Launch the web oscilloscope, and set frequency view | |
===Videos=== | ===Videos=== | ||
| Zeile 340: | Zeile 241: | ||
#[https://www.youtube.com/watch?v=NIer_kITelc Perimeter wire and matched filter theory (German)] | #[https://www.youtube.com/watch?v=NIer_kITelc Perimeter wire and matched filter theory (German)] | ||
#[https://www.youtube.com/watch?v=VxJN2xb55dU&feature=youtu.be Sender PCB] | #[https://www.youtube.com/watch?v=VxJN2xb55dU&feature=youtu.be Sender PCB] | ||
| + | #[http://www.youtube.com/watch?v=FGaUSg-uUxk Perimeter stop test] | ||
| + | #[http://www.youtube.com/watch?v=8R8QaffNlJw Perimeter tracking test] | ||
| + | #[http://www.youtube.com/watch?v=CftrnetFVYc&feature=youtu.be Finding and tracking test L50] | ||
| + | #[http://www.youtube.com/watch?feature=player_embedded&v=fjuQViS2rHM Finding and tracking test Rotenbach] | ||
| + | #[http://youtu.be/r4ZMgasMkH0 Magnetic field demonstration video] | ||
=Tracking of perimeter= | =Tracking of perimeter= | ||
| Zeile 351: | Zeile 257: | ||
You can find more information about PID controllers here: | You can find more information about PID controllers here: | ||
[http://www.ardumower.de/index.php/de/forum/anleitungen-hilfe/121-pid-regelung-fuer-drehzahl-drehung-etc-richtig-einstellen Forum]. | [http://www.ardumower.de/index.php/de/forum/anleitungen-hilfe/121-pid-regelung-fuer-drehzahl-drehung-etc-richtig-einstellen Forum]. | ||
| Zeile 359: | Zeile 262: | ||
#[http://grauonline.de/wordpress/?page_id=364 More details about the matched filter] | #[http://grauonline.de/wordpress/?page_id=364 More details about the matched filter] | ||
#[http://www.grauonline.de/alexwww/ardumower/oscilloscope/oscilloscope.html Sound card oscilloscope including matched filter] | #[http://www.grauonline.de/alexwww/ardumower/oscilloscope/oscilloscope.html Sound card oscilloscope including matched filter] | ||
Perimeter
Sender principle:
Receiver principle:
- A coil receives the signal
Sender software
Your perimeter wire resistance (R): 12 Ohm Your adjusted voltage at the DC/DC converter: 8 Volt
Current: I = U / R = 8 Volt / 12 Ohm => 0.7 Ampere Power: P = U * I = 8 Volt * 0.7 Ampere => 5.6 Watt
Sender diagnostics
Receiver
Signal measurements
Receiver ADC calibration
- Perimeter2 demo
- 120m perimeter wire test
- Sender PCB
- Perimeter stop test
- Perimeter tracking test