(→Download and flash Arduino code) |
(→Test requirements) |
| (127 dazwischenliegende Versionen desselben Benutzers werden nicht angezeigt) | |||
| − | This page describes how to flash the Arduino, configure the robot mower and look for errors. | + | This page describes how to flash the Arduino for your robot mower, configure the robot mower and look for errors. |
| − | = | + | =Test requirements= |
| + | [[File:warning.png]]Security note: For security reasons, always remove mower blades in your first tests! | ||
| − | + | [[File:warning.png]]Important: For your first wheel motor tests, jack your robot so that the tires can run freely without ground contact! | |
| − | + | [[File:warning.png]] '''Warning: All software, hardware and motor components are designed and optimized as a whole, if you try to replace or exclude some component not as designed, you risk to damage your hardware with the software.''' | |
| − | + | =Uploading the firmware to your Arduino= | |
| + | <b>NOTE</b>: If you have never worked with Arduino before, read our <b>[http://wiki.ardumower.de/index.php?title=Arduino_first_steps 'Arduino first steps' introduction]</b> (it also contains useful information if uploading does not work). | ||
| + | 1. Download a <b>Firmware Release</b> at [https://github.com/Ardumower/ardumower/releases Github] | ||
| + | 2. Download the [http://arduino.cc/en/Main/Software <b>Arduino IDE</b>] that we will use to upload the firmware to your Arduino | ||
| + | 3. Start Arduino IDE, and choose the right <b>Arduino board</b> (either Mega 2560 or Due (recommended) - <b>for Due: choose 'USB programming port'</b>) | ||
| + | 4. In file 'mower.h', choose the correct <b>PCB</b> (PCB_1_2 or PCB_1_3) - Example for choosing PCB 1.3 (a line started with // will be ignored): | ||
| + | // #define PCB_1_2 | ||
| + | #define PCB_1_3 | ||
| + | 5. In file 'mower.h', choose the correct <b>robot type</b> (ROBOT_ARDUMOWER or ROBOT_MINI) | ||
| + | 6. In file 'mower.h', choose the correct <b>motor drivers</b> (DRIVER_MC33926 or DRIVER_L298N) - in most cases, DRIVER_MC33926 is the correct one | ||
| + | 7. If you do not want the robot to monitor battery and charging voltage, set 'batMonitor = 0' in mower.cpp. | ||
| + | 8. <b>Upload</b> the code to your Arduino board | ||
=Settings= | =Settings= | ||
| − | The robot uses settings that you can adjust for your own robot and environment (via | + | The robot uses settings that you can adjust for your own robot and environment (via the code or via pfod App). The default settings (factory settings) are stored in the config file 'mower.cpp'. In this file you can find descriptions for all settings. |
| − | + | After you modified any settings via serial console or via pfod App, these settings have higher priority. However, you can go back to default settings (or any uploaded settings) by a factory reset. | |
| + | [[File:warning.png]] <b>Important: If you upload a new Firmware version into your robot and you do not want to use any old/modified settings, you have to reset all settings (via pfodApp: 'Settings->Factory reset' or via console 'main menu->load factory settings'), so any uploaded settings take place. </b> | ||
| Zeile 20: | Zeile 43: | ||
| − | + | =Serial console= | |
| + | After successfully uploading, open the Arduino IDE <b>serial console</b> and choose baud rate 19200. You should see something like this. If all you get is an error line instead, please read the troubleshooting section. | ||
| + | ADCMan: found calib data | ||
| + | ---ADC calib--- | ||
| + | ADC sampleRate=38462 | ||
| + | AD0 min=9999 max=-9999 diff=-19998 ofs=334 | ||
| + | AD1 min=9999 max=-9999 diff=-19998 ofs=417 | ||
| + | SETUP | ||
| + | matchSignal size=24 | ||
| + | subSample=4 | ||
| + | capture size=192 | ||
| + | 1 0 -1 0 1 -1 1 -1 0 1 -1 1 0 -1 0 1 -1 0 1 -1 0 1 0 -1 | ||
| + | IMU error: no calib data | ||
| + | accOfs=0.00,0.00,0.00 | ||
| + | accScale=2.00,2.00,2.00 | ||
| + | comOfs=0.00,0.00,0.00 | ||
| + | comScale=2.00,2.00,2.00 | ||
| + | initL3G4200D | ||
| + | gyro read error | ||
| + | loadSaveErrorCounters: read | ||
| + | loadSaveErrorCounters addrstop=423 | ||
| + | loadUserSettings | ||
| + | EEPROM USERDATA: NO EEPROM USER DATA | ||
| + | PLEASE CHECK AND SAVE YOUR SETTINGS | ||
| + | loadSaveRobotStats: read | ||
| + | loadSaveRobotStats addrstop=822 | ||
| + | START | ||
| + | Ardumower 1.0a8-Azurit-dev PCB 1.3 Arduino Mega IOREF=5.00 | ||
| + | Robot: Mini | ||
| + | press... | ||
| + | d for menu | ||
| + | v to change console output (sensor counters, values, perimeter etc.) | ||
| + | sen_counters | ||
| + | t 1 L 0 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 677.0 chg 677.0 0.0 imu 0 adc 0 Mini | ||
| − | = | + | =Motor test= |
| + | In this motor test we will make sure that the motors are controlled in the right direction. | ||
| − | + | 1. In Arduino IDE serial console, press 'd' and ENTER to get the main menu - you should see something like this: | |
| − | 2 | + | MAIN MENU: |
| − | + | 1=test motors | |
| − | + | 2=test odometry | |
| − | + | 3=communications menu | |
| − | + | 5=calibrate IMU acc next side | |
| + | 7=delete IMU calib | ||
| + | c=test RTC | ||
| + | l=load factory settings | ||
| + | r=delete robot stats | ||
| + | x=print settings | ||
| + | 0=exit | ||
| − | + | 2. Press '1' and ENTER for motor test. Motors left and right should turn in the shown directions. | |
| − | + | testing left motor (forward) half speed... | |
| − | + | t 741 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | |
| − | 9 | + | t 742 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini |
| + | t 743 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 744 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 745 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | testing left motor (reverse) full speed... | ||
| + | t 747 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 748 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 749 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 751 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 752 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | testing right motor (forward) half speed... | ||
| + | t 754 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 755 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 756 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 757 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 758 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | testing right motor (reverse) full speed... | ||
| + | t 760 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 761 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 762 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 763 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| + | t 764 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini | ||
| − | + | If the wrong motor is turning, exchange left and right motor wires. If one motor is not turning in the right direction, exchange the motor wires (+/-). | |
| − | + | =Odometry= | |
| − | + | 1. Make sure that you have connected all motor odometry cables to your PCB. Now we will test the encoders and connections. In the main menu (see above), choose '2' to test odometry. Both left and right odometry counters should start to increase about the same speed like shown below: | |
| − | + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution, '0' exit left=0 right=0 | |
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution, '0' exit left=1 right=1 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution, '0' exit left=2 right=1 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution, '0' exit left=3 right=2 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution, '0' exit left=4 right=3 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution, '0' exit left=6 right=4 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution, '0' exit left=7 right=5 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution, '0' exit left=8 right=6 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution, '0' exit left=9 right=7 | ||
| − | + | Slightly block one wheel with your hands to see if the correct odometry counter (left or right) is reducing speed. If the wrong side is reducing speed, exchange odometry cables. | |
| − | + | 2. Choose 'o' to test a full wheel revolution. The wheels should make one turn and stop about at the starting position like shown below (in this example I'm using an Ardumower Mini and PCB1.3): | |
| − | + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=0 right=0 | |
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=0 right=1 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=1 right=1 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=1 right=2 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=2 right=2 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=3 right=2 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=3 right=3 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=4 right=3 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=4 right=4 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=5 right=4 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=5 right=5 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=6 right=5 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=7 right=5 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=7 right=6 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=8 right=6 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=8 right=7 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=9 right=7 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=9 right=8 | ||
| + | Press'f' forward, 'r' reverse, 'z' reset, 's' stop, 'o' one revolution left=10 right=8 | ||
| − | + | 3. Choose '0' and ENTER to get back to the main menu. | |
| + | =First run= | ||
| + | After motor test and odometry test were successful, we can do a first test run. | ||
| + | [[File:warning.png]]Important: For your first robot test, jack your robot so that the tires can run freely without ground contact! | ||
| + | To start the mower, you need to add a button and a buzzer. There are several modes (you have to press and hold the button for x beeps long): | ||
1 beeps : Normal mowing (using blade modulation if available) | 1 beeps : Normal mowing (using blade modulation if available) | ||
2 beeps : Normal mowing (without blade modulation) | 2 beeps : Normal mowing (without blade modulation) | ||
| Zeile 79: | Zeile 188: | ||
5 beeps : Find perimeter and track it | 5 beeps : Find perimeter and track it | ||
| − | + | Press the button for '1 beep', and the robot's wheels should start turning forward (switching from state OFF to state FORW) as shown below: | |
| − | + | t 2 L5731 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.3 0.9 imu 0 adc 97 Mini | |
| − | + | t 0 L5942 m0 FORW rpm 0 0 set 50 50 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.3 0.9 imu 0 adc 0 Mini | |
| − | + | t 0 L5942 m0 FORW rpm 60 60 set 50 50 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.3 0.9 imu 0 adc 90 Mini | |
| − | + | t 1 L3764 m0 FORW rpm 60 60 set 50 50 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.3 0.9 imu 0 adc 97 Mini | |
| − | + | t 2 L4160 m0 FORW rpm 60 60 set 50 50 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.3 0.9 imu 0 adc 97 Mini | |
| + | If it does not stay in the 'FORW' state for at least one minute, probably a sensor will make a false trigger and you have to fine-tune the settings for that sensor. | ||
| − | + | =Sensor counters and sensor values= | |
| + | There are different views for your sensors: | ||
| − | + | m0 - sensor trigger counters (default view) | |
| − | + | m1 - current sensor values | |
| + | m2 - perimeter values | ||
| − | t 4 | + | You can change the view by pressing 'v' and ENTER. You will see the selected view in the console as shown below: |
| − | t 5 | + | |
| + | t 4 L177 <b>m0</b> ... | ||
| + | There is a counter for each sensor. Once a sensor triggers, the corresponding counter increases. In the example below the mower motor current overflow triggered, and so the mower motor sensor counter increases. Additionally, the robot switches from state 'FORW' (forward) to the new state 'REV' (reverse): | ||
| + | t 4 L177 m0 FORW spd 33 33 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 20.8 chg 21.7 0.0 imu 0 adc 0 Ardumower | ||
| + | t 5 L177 m0 REV spd -26 -26 0 sen 0 0 1 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 20.8 chg 21.7 0.0 imu 0 adc 1 Ardumower | ||
Here is a description of each column: | Here is a description of each column: | ||
| − | t - time of current machine state (ms) | + | t - time of current machine state (FORW, REV, ROLL, etc.) (ms) |
| − | + | L - loop () - cycles per second | |
| − | + | m - console output mode (0 = sensor trigger counters / 1 = current sensor values / 2 = perimeter values) | |
| − | + | spd - current motor speed left and right wheels | |
| − | - | + | set - set point values for motor wheels speed control |
| − | + | sen - motor current overflow counter: left wheel, right wheel, mower motor | |
| − | sen - motor current overflow counter: left, right, mower | + | |
bum - bumper counter: left, right | bum - bumper counter: left, right | ||
son - ultrasonic distance-below: counter | son - ultrasonic distance-below: counter | ||
| − | pit, roll - inclination (calculated with | + | pit, roll - inclination (calculated with IMU/accel sensor) |
yaw - compass course | yaw - compass course | ||
bat - battery voltage | bat - battery voltage | ||
chg - charger voltage sensor | chg - charger voltage sensor | ||
| − | + | =Console commands= | |
| − | + | You can manually trigger sensors via the console. Also, you can set the robot into a specific state. | |
'd': menu for testing, adjust IMU, Bluetooth | 'd': menu for testing, adjust IMU, Bluetooth | ||
| Zeile 137: | Zeile 249: | ||
'1': Automode motorMowEnable | '1': Automode motorMowEnable | ||
| + | =Bluetooth module= | ||
| − | + | [[File: Ardumower_live_monitoring_configuration_debugging.jpg | 400px]] | |
| − | File: | + | |
| − | + | The Ardumower can be monitored and controlled via an Android device (phone/tablet). Before you can use the Android App, you have to configure the bluetooth module on the robot so it matches the baud rate in the robot code (mower.h). | |
| − | The | + | |
| − | + | 1. Plug-in the bluetooth module (HC-05) on the PCB at the position where the bluetooth module pinout matches the PCB pinout. | |
| − | + | 2. <b>Press and hold the micro KEY button on the bluetooth module while powering-on the PCB (and bluetooth module)</b>. The bluetooth LED should blink slowly now. | |
| − | + | 3. Start the Arduino IDE serial console, choose 19200 baud and press 'd' and ENTER to enter the main menu. | |
| − | + | 4. Press '3' and ENTER to get into the communications menu - you should get something like this: | |
| − | + | COMMUNICATIONS MENU == Bluetooth == | |
| − | + | 1=Select other communication method | |
| − | + | 2=setup BT module config (quick baudscan (recommended)) | |
| − | + | 3=setup BT module config (extensive baudscan) | |
| − | + | 0=Main Menu | |
| − | + | 5. Press '2' and ENTER to run the bluetooth module config - you should see several 'success' lines as shown below: | |
| − | = | + | trying baudrate 38400 config 0... |
| + | send: AT | ||
| + | send: AT | ||
| + | received: OK | ||
| + | =>success | ||
| − | + | detecting BT type... | |
| + | send: AT+VERSION | ||
| + | send: AT+VERSION? | ||
| + | received: +VERSION:2.0-20100601 | ||
| + | OK | ||
| + | =>must be a HC03/04/05 ? | ||
| − | = | + | setting name Mini... |
| − | + | send: AT+NAME=Mini | |
| − | + | received: OK | |
| − | + | =>success | |
| − | + | setting pin 1234... | |
| − | + | send: AT+PSWD=1234 | |
| + | setting baudrate 19200... | ||
| + | send: AT+UART=19200,0,0 | ||
| + | =>success | ||
| + | You may restart BT module now! | ||
| + | 6. After the module has been properly configured, re-power (power off and on) the PCB (or bluetooth module). | ||
| + | 7. Download the App [https://play.google.com/store/apps/details?id=de.grauonline.arduremote 'ArduRemote'] on your Android device. Alternatively, you can use the App [https://play.google.com/store/apps/details?id=au.com.forward.pfodApp 'pfodApp']. | ||
| + | 8. You need to pair the bluetooth module it with your Android device. On the Android device, choose symbol "Settings" (via Android menu). Now choose "Wirless and Networks->Bluetooth Settings" and "Find device". Finally, choose "pair with this device" and enter your pin ("1234"). The Bluetooth module should now appear as "paired". Try to connect using ArduRemote App with your robot. You should get a menu like this on your Android device: | ||
| + | [[File: Arduremote_ardumower.png | 200px]] | ||
| + | In the serial console on your PC, you should see the commands sent from your Android App: | ||
| + | Pfod cmd= {.} | ||
| Zeile 202: | Zeile 324: | ||
Processing can be downloaded here: https://processing.org/ | Processing can be downloaded here: https://processing.org/ | ||
===Sensor logging=== | ===Sensor logging=== | ||
| Zeile 225: | Zeile 340: | ||
| − | = | + | = Motor controller (PID) = |
| − | + | The speed of the motors is controlled by a software PID controller. You can monitor the quality of the motor speed control via pfodApp (Plot->Motor control): | |
| − | File: | + | File: Odometry_motor_pid_controller.png |
| − | == | + | =Charging= |
| − | + | The battery voltage can be monitored (Battery->Monitor->YES). So it can be determined when the robot should go to the charging station. Via charging contacts, the robot can detect if has reached the charging station. | |
| − | + | Via pfodApp (Android) you can monitor the charging process. | |
| − | File: | + | File: Ardumower_battery_plotting.jpg | Charging plot |
| + | File: Ardumower_battery_settings.png | Battery settings | ||
| + | File: Ardumower_charging_battery_full.jpg | Battery fully charged | ||
| + | File: Ardumower_charging_timeout.png | Charging with timeout | ||
| − | + | = Timer/RTC = | |
| + | 1. For time-controlled mowing the RTC module should work successfully. Test the RTC module by entering the main menu (press 'd' and ENTER) and then press 'c' and ENTER for the RTC test: | ||
| − | + | MAIN MENU: | |
| + | 1=test motors | ||
| + | 2=test odometry | ||
| + | c=test RTC | ||
| − | + | During this test, a test date will be written to the RTC module and read back. The read back date should match the test date. This indicates the RTC module works successfully. | |
| − | + | 2. To activate time-based mowing, set 'Timer->Use->YES' (via Android pfodApp), set the current date and time, and define one or more timers. | |
| − | + | <b>Important: </b>If you activate 'GPS->Use->YES', the current date and time will be set via GPS and not via RTC clock. | |
| − | + | On the robot, several timers can be programmed (via Android pfodApp). | |
| − | + | For each timer, you can define a time interval ('time windows') for the desired days. As long as the actual time is within any time window, the robot can freely mow, charge, mow, charge etc. | |
| + | === Example: === | ||
| − | + | Timer 1: 08:00 - 13:00 Monday, Thuesday, Wednesday | |
| − | + | Timer 2: 14:00 - 16:00 every day | |
| + | Timer 3: off | ||
| − | + | Timer 4: off | |
=IMU= | =IMU= | ||
| Zeile 524: | Zeile 502: | ||
| − | + | 2. Then activate the perimeter in the Ardumower software (pfodApp->Options->Perimeter Use: YES). It is recommended to keep the default perimeter settings. | |
The perimeter settings are: | The perimeter settings are: | ||
| Zeile 550: | Zeile 532: | ||
| − | [[File:warning.png]] The ADC calibration ensures that the zero point (silence) is detected correctly, and so later the received signal is symmetric around zero. | + | [[File:warning.png]] <b>Before the perimeter receiver can be used, the ADC pin has to be calibrated. The ADC calibration ensures that the zero point (silence) is detected correctly, and so later the received signal is symmetric around zero.</b> |
| − | # Run the ADC calibration once ("pfodApp->ADC Calibration") | + | # Run the ADC calibration once ("pfodApp->ADC Calibration" or via serial console 'main menu->ADC calib') |
When calibrated correctly, the signal in the pfodApp plot ('sig') should be around zero (0) when the perimeter sender is switched off. When the perimeter sender is switched on, the plotted signal ('sig') should have the same maximum amplitude for both positive and negative axis (is 'symmetric around zero'). | When calibrated correctly, the signal in the pfodApp plot ('sig') should be around zero (0) when the perimeter sender is switched off. When the perimeter sender is switched on, the plotted signal ('sig') should have the same maximum amplitude for both positive and negative axis (is 'symmetric around zero'). | ||
| Zeile 636: | Zeile 618: | ||
=== GPS error === | === GPS error === | ||
Typical GPS error is 2-5 meters (at a sample rate of 1 Hz). As this is not sufficient as a replacement for a perimeter wire, GPS can only be seen as an extension or for global navigation (navigation from one lawn to another lawn). | Typical GPS error is 2-5 meters (at a sample rate of 1 Hz). As this is not sufficient as a replacement for a perimeter wire, GPS can only be seen as an extension or for global navigation (navigation from one lawn to another lawn). | ||
=Drop sensor= | =Drop sensor= | ||
| Zeile 708: | Zeile 675: | ||
*If obstacle during reverse => roll | *If obstacle during reverse => roll | ||
*If obstacle during roll => forward | *If obstacle during roll => forward | ||
| + | =How to report a new bug/new feature/new code= | ||
| + | Click on [https://github.com/Ardumower/ardumower/issues/new?title=Error+XYZ+%2F+Fehler+XYZ&body=Please+always+fill-in+below%2FBitte+unbedingt+ausf%C3%BCllen%21%0D%0A%0D%0A--English--%0D%0AYour+battery+voltage+%2812v%2C+24v%29%3A+24v%0D%0AYour+gear+motor+%28Ardumower%2C+other%29%3A+Ardumower+motor%0D%0AYour+Ardumower+software+version+%28pfodApp-%3EInfo%29%3A+890%0D%0AYour+Arduino+%28Mega+or+Due%29%3A+Mega+2560%0D%0AYour+PCB+version+%28printed+on+PCB%29%3A+0.5%0D%0AYour+PCB+mounted+parts+configuration+%28default+or+custom+and+how%29%3A+default%0D%0AOdometry+sensor+%28yes%2Fno%29%3F+yes%0D%0AArdumower+chassis+%28yes%2Fno%29%3F+yes%0D%0AExact+error+description%3A+...+%0D%0A%0D%0A--Deutsch--%0D%0ADeine+Akku-Spannung+%2812v%2C+24v%29%3A+24v%0D%0ADein+Antriebsmotor+%28Ardumower%2C+anderer%29%3A+Ardumower+Motor%0D%0ADeine+Ardumower-Software+Version%3A+%28pfodApp-%3EInfo%29%3A+890%0D%0ADeine+PCB-Version+%28siehe+Aufdruck%29%3A+0.5%0D%0ADein+Arduino+%28Mega+oder+Due%29%3A+Mega+2560%0D%0ADeine+PCB+Bauteilbest%C3%BCckung+%28Standard+oder+abweichend+und+wie%29%3A+Standard%0D%0AOdometrie+sensor+%28ja%2Fnein%29%3F+ja%0D%0AArdumower+Chassis+%28ja%2Fnein%29%3F+ja%0D%0AGenaue+Fehlerbeschreibung%3A+...%0D%0A 'this link'] and create a new issue - Please let us know: | ||
| + | Your platform version (Arduino Mega 2560, Arduino Due) | ||
| + | Your Arduino IDE version (latest code requires 1.6.3) | ||
| + | Your exact operating system (Windows 8, Linux etc.) | ||
| + | Your Ardumower code version (for a list of releases see https://github.com/Ardumower/ardumower/releases) | ||
| + | Any other information that may be useful... | ||
| + | =Diagnostics/troubleshooting= | ||
| + | ===Sensor errors=== | ||
| + | Each time a sensor triggers, its corresponding sensor counter increases. The sensor trigger counters as well as the current sensor values can be viewed on the serial console. The following values are shown for the trigger counters in the serial console: | ||
| + | # Time of state machine's state (ms) | ||
| + | # loop()-counts per second | ||
| + | # choosen Verbose-Mode (0=counter readings/1=current values/2=current values) | ||
| + | # current state machine state (FORW, REV, ROLL etc.) | ||
| + | # drive home? (1/0) | ||
| + | # "spd" - Control/speed motors: left (PWM), right (PWM), mower (RPM) | ||
| + | # "sen" - Current limit exceeded counter motors: left, right, mower | ||
| + | # "bum" - bumper counter: left, right | ||
| + | # "son" - Ultrasonic-distance threshold exceeded (counter) | ||
| + | # "pit/roll" - Tilt (computed by acceleration sensor) | ||
| + | # "com" - compass course | ||
| + | # "per" - Perimeter loop detected: counter | ||
| + | # "bat" - Battery voltage | ||
| + | # "chg" - Charging current | ||
| + | Using the key 'v', you can toggle between sensor trigger counters and current sensor values. | ||
| + | [[File:warning.png]] Additionally, you can use pfodApp (Android) to plot the sensors (trigger counters and current values) over time. This allows you to wirelessly monitor your robot mower for error diagnostics. It is highly recommended. | ||
| + | <gallery> | ||
| + | File:Ardumower_sensor_counter_plotting.jpg |Sensor trigger counters | ||
| + | File:Ardumower_plot_sensors.jpg |Sensor measurement values | ||
| + | ===Hardware measurements=== | ||
| + | Tutorial for pocket oscilloscopes: | ||
| + | ===Error codes=== | ||
| + | If your robot beeps periodically (every 5 sec one short beep), it is in ERROR state. Either run the serial console or 'pfodApp->Error Counters' to find out the detailed error. The possible solutions for each error are given below. For details about your robot settings, see [http://wiki.ardumower.de/index.php?title=Ardumower_PCB#Settings Settings]. | ||
| + | ERR_MOTOR_LEFT Left gear motor error | ||
| + | * Check gear motor driver module and left gear motor (supply voltage, signal lines) | ||
| + | * MC33926: ensure SLEW jumper is not set | ||
| + | * Tracking: reduce Motor-Max-PWM and Tracking-P to reduce EMF | ||
| + | ERR_MOTOR_RIGHT Right gear motor error | ||
| + | * Check gear motor driver module and right gear motor (supply voltage, signal lines) | ||
| + | ERR_MOTOR_MOW Mower motor error | ||
| + | * Check mower motor driver module and mower motor (supply voltage, signal lines) | ||
| + | * Reduce Motor-Max-Power, so over-current is detected earlier | ||
| + | ERR_MOW_SENSE Mower motor over-current | ||
| + | * Check mower motor driver module and mower motor | ||
| + | * Increase Motor-Max-Power, so over-current is detected later | ||
| + | ERR_IMU_COMM IMU communication error | ||
| + | * Check IMU module connections | ||
| + | ERR_IMU_CALIB IMU calibration error | ||
| + | * Start IMU calibration (either via Console or pfodApp->Settings->IMU) | ||
| + | ERR_IMU_TILT IMU tilt error | ||
| + | * Check IMU module and robot orientation | ||
| + | ERR_RTC_COMM RTC communication error | ||
| + | * Check RTC module connections, RTC battery etc. | ||
| + | ERR_RTC_DATA RTC corrupt data error | ||
| + | * Set and save RTC date and time | ||
| + | * If the error repeats, change RTC battery | ||
| + | ERR_PERIMETER_TIMEOUT Perimeter signal timeout | ||
| + | * Check perimeter sender, wire etc. | ||
| + | * Check coil polarity | ||
| + | * Reduce Perimeter-smag, so timeout is higher | ||
| + | * Increase Perimeter-timeout-seconds, so timeout is higher | ||
| + | * Check your signal-to-noise ratio is higher than 1.0 | ||
| + | ERR_TRACKING Perimeter tracking error | ||
| + | * Increase Perimeter-tracking-timeout, so timeout is higher | ||
| + | ERR_ODOMETRY_LEFT Left motor odometry error | ||
| + | * Check left odometry cable | ||
| + | * Check left motor direction | ||
| + | ERR_ODOMETRY_RIGHT Right motor odometry error | ||
| + | * Check right odometry cable | ||
| + | * Check right motor direction | ||
| + | ERR_BATTERY Battery error | ||
| + | * Check battery connections | ||
| + | ERR_CHARGER Charger error | ||
| + | * Check charger connections | ||
| + | ERR_GPS_COMM GPS communication error | ||
| + | * Check GPS cables | ||
| + | ERR_GPS_DATA GPS data error | ||
| + | * Check GPS antenna and cable | ||
| + | ERR_ADC_CALIB ADC calibration error | ||
| + | * Start ADC calibration (either via Console or pfodApp->ADC calibration) | ||
| + | ERR_EEPROM_DATA EEPROM data error | ||
| + | * Save user settings (either via Console or pfodApp->Settings-Save) | ||
| + | After fixing the error, you can delete errors: | ||
| + | Console: | ||
| + | press... | ||
| + | d for menu | ||
| + | ===I2C errors=== | ||
| + | If you get an error in the console ('I2C bus error. Could not clear. SCL clock line held low'), the I2C bus is not working properly. Reasons can be: RTC module is missing or a general I2C bus error. | ||
| + | Ensure the I2C bus is working correctly. A console stucked at line 'initL3G4200D' indicates I2C is not working correctly. If there's a communication problem or another serious problem, the error counter increases. The error counter can be monitored via pfodApp. Additionally, the robot mower will beep when started. | ||
| + | Several components (Arduino Nano, RTC, IMU, etc.) are communicating via the I2C bus (SDA/SCL wires). These wires should be very short (maybe even twisted) and they should be far away from DC converter and motor drivers. If there's a communication problem, the error counter will increase and robot will beep when started. The error counter can be monitored via pfodApp. | ||
| + | ===Arduino errors=== | ||
| + | ===Disable all pins not connected=== | ||
| + | Ensure that you have disabled all features and pins in the robot configuration that are not connected (not used). | ||
| + | Example: If you do not have connected odometry pins, disable them in the robot config (robot.cpp): | ||
| + | odometryUse = 0; // use odometry? | ||
| + | ===Motors working correctly=== | ||
| + | Run the serial console (Arduino IDE: CTRL+SHIFT+M, 19200 Baud) and press 'd' and ENTER for menu. Then press '1' and ENTER to run the motor test. | ||
| + | ===Any unexpected sensor triggering=== | ||
| + | If your robot does something unexpected, it might be a sensor that is incorrectly triggering. Check this via the serial console: | ||
| + | Run the serial console (Arduino IDE: CTRL+SHIFT+M, 19200 Baud), and start the robot. Each time a sensor triggers, the counter of that sensor will increase. See description of each sensor below. | ||
| + | Now when your robot does something unexpected, have a look which of the sensor counters increased to locate the problem. | ||
| + | ===Some sensor not triggering?=== | ||
| + | ===Bluetooth not connecting?=== | ||
| + | * Verify that BT module baudrate is configured properly (using Ardumower Console) - activate programming button on BT module for programming procedure. | ||
| + | * Verify that BT module is 'paired' on your Android phone | ||
| + | * Verify that Arduino Mega is not powered via USB (but DC/DC instead) | ||
| + | ===Robot not stopping to rotate when reaching perimeter (home mode)=== | ||
| + | At first, verify that the perimeter tracking itself is working: Manually put the robot on the perimeter wire, and via ArduRemote App, choose 'Commands->Track' and verify the robot is tracking the perimeter. If it does not, adjusting the tracking PID parameters may help. | ||
| + | The position of the coil should be as indicated here: | ||
| + | <gallery> | ||
| + | If the robot runs over the perimeter wire (coil is then "outside" of perimeter loop) it will try to get "inside" the loop again by rotating. If getting the coil "inside" the loop by rotating is not possible, the robot will rotate endless. | ||
| + | The more the robot runs over the perimeter, the more difficult it is to get "inside" again by rotation. The robot speed should be reduced as well as moving the coil further outside. | ||
| + | NOTE: It's always a good idea to manually place the robot at the position where you saw the robot detecting the perimeter. The perimeter plot should change from "in" to "out" at that position (http://wiki.ardumower.de/index.php?title=Perimeter_wire#Receiver_diagnostics.2Ftroubleshooting). Then manually rotate the robot (without motor) at that position and verify that "out" changes again to "in". If that is not the case, the position of the coil is not OK or the robot drives too quickly and detects the perimeter too late. | ||
| + | ===More troubleshooting=== | ||
| + | #[[Änderungen der Konfigurationseinstellungen in der Mower.cpp Datei werden nicht übernommen]] | ||
| + | #[[Der Ladestrom im ArduMower zeigt nichts oder falsche Werte an]] | ||
| + | #[[Der Perimetersender ohne automatische Regelung]] | ||
| + | #[[Elektrische Fehlersuche am BT Modul]] | ||
| + | #[[Programmieranleitung für das Bluetooth Modul auf der Platine V1.2]] | ||
- 1 Test requirements
- 3 Settings
- 4 Serial console
- 5 Motor test
- 6 Odometry
- 7 First run
- 9 Console commands
- 10 Bluetooth module
- 11 Motor controller (PID)
- 12 Charging
- 13 Timer/RTC
- 14 IMU
- 15 IMU calibration steps
- 16 Perimeter receiver
- 17 GPS
- 18 Drop sensor
- 19 Finite state machine
- 21.1 Sensor errors
- 21.2 Hardware measurements
- 21.3 Error codes
- 21.4 I2C errors
- 21.5 Arduino errors
- 21.12 More troubleshooting
Serial console
Motor test
testing left motor (forward) half speed... t 741 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 742 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 743 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 744 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 745 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini testing left motor (reverse) full speed... t 747 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 748 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 749 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 751 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 752 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini testing right motor (forward) half speed... t 754 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 755 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 756 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 757 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 758 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini testing right motor (reverse) full speed... t 760 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 761 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 762 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 763 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini t 764 L5790 m0 OFF rpm 0 0 set 0 0 sen 0 0 0 bum 0 0 dro 0 0 son 0 yaw 0 pit 0 rol 0 bat 6.8 chg 0.1 0.9 imu 0 adc 0 Mini
Odometry
First run
t 4 L177 m0 ...
Console commands
Bluetooth module
Pfod cmd= {.}
Sensor logging
Charging
Timer/RTC
Timer 3: off
Timer 4: off
IMU
IMU sensor fusion
- Compass sensor: HMC5883L
- Gyro: L3G4200D
Calibration quality test
Perimeter receiver
GPS
Currently, GPS is used
Visualization of GPS data
GPS error
Drop sensor
Einstellung im Sketsch:
Verdrahtung:
Dropcontact = 1; ändern in 0
Implemented updates:
Sensor errors
- loop()-counts per second
- drive home? (1/0)
- "com" - compass course
- "bat" - Battery voltage
- "chg" - Charging current
Error codes
* Check GPS cables